Underwriting the residual on a 6 kW per rack building in a 60 kW world
Chasing a question I can't settle. A facility built around 2014 for something like 6 to 8 kW per rack, air cooled, decent connectivity, on a feed with modest headroom. Fully leased today at rents that look fine. The seller's residual assumption is a modest cap rate expansion off in-place rent at year ten.
My problem is that the workloads driving all the demand everyone talks about don't fit in that building. High density AI racks want liquid cooling and a power density the floor was never designed for, and the retrofit isn't a chiller swap. It's floor loading, containment, distribution, sometimes the roof. So the residual buyer in year ten is either an enterprise tenant with ordinary workloads, which is a shrinking but real pool, or a developer buying the parcel and the interconnection and gutting the building.
Two defensible ways to underwrite that. Value the shell and the fit-out on remaining useful life, accept obsolescence, and hold rents flat with a wide exit cap. Or ignore the building almost entirely and value the interconnection capacity plus the fiber routes plus the land, on the argument that in a market where power delivery takes years, an energized site with existing capacity is worth more than the box sitting on it, and the box just has to cover carry until somebody wants the site.
Those two paths give me residuals about 40% apart on the same asset. Which one would you actually put in the model?
How do you set the year-ten residual on a low-density legacy facility?